Do you think Tesla will release a GEN 4 Wall Connector for the Cybertruck due to the larger potential battery?

The Cybertruck will be my first EV and I don’t want to get the GEN 3 installed too early, just in case Tesla releases a bigger/better charger. If the battery is north of 150 kHw, it would take awhile to charge up a low battery. At 150 kHw, your looking somewhere around 13 hours. At 180kHw, your looking at 15.5 hours.

Thoughts?
 
Last edited:

Cyberman

Well-known member
First Name
Adam
Joined
Apr 7, 2020
Threads
31
Messages
2,099
Reaction score
764
Location
San Diego
Vehicles
F150,F550, Escape
Occupation
Cybercontractor
Country flag
Do you think Tesla will release a GEN 4 Wall Connector for the Cybertruck due to the larger potential battery?

The Cybertruck will be my first EV and I don’t want to get the GEN 3 installed too early, just in case Tesla releases a bigger/better charger. If the battery is north of 150kw, it would take awhile to charge up a low battery. At 150kw, your looking somewhere around 13 hours. At 180kw, your looking at 15.5 hours.

Thoughts?
(Sigh) By the time Cybertruck reaches production, they'll probably have Gen 5 chargers...
 

Jhodgesatmb

Well-known member
First Name
Jack
Joined
Dec 1, 2019
Threads
82
Messages
5,201
Reaction score
1,986
Location
San Francisco Bay area
Website
www.arbor-studios.com
Vehicles
Tesla Cybertruck FS AWD, Tesla Model Y LR
Occupation
Retired AI researcher
Country flag
You meant to say 150 KwH. In the early days of the Model S/X one could charge at a higher amperage than the current maximum of 48 amps. The Tesla chargers can be configured to other amperages but the car has to be able to handle it. Also, some say that the 4680 cells might be able charge faster. These two things might allow a 150 KwH battery pack to charge faster w/o changing the charger...but we will see.
 

android04

Well-known member
First Name
Dario
Joined
Jul 28, 2020
Threads
2
Messages
292
Reaction score
269
Location
Crete, NE
Website
ts.la
Vehicles
2023 Tesla Model Y LR AWD w/Boost, 2018 Tesla Model 3 LR RWD
Country flag
If the Cybertruck can take more than 48A while charging on Level 2 then I'm sure Tesla will offer an updated Wall Connector to match. Otherwise people will have to buy Gen 2 Tesla Wall Connectors that can output up to 80A (or a non-Tesla EVSE that can output more than 48A). There aren't enough Gen 2 Tesla Wall Connectors to go around, and Tesla isn't making them anymore.
 

anionic1

Well-known member
First Name
Michael
Joined
Apr 30, 2021
Threads
27
Messages
1,518
Reaction score
326
Location
California
Vehicles
Cybertruck
Occupation
Estimator
Country flag
Do you think Tesla will release a GEN 4 Wall Connector for the Cybertruck due to the larger potential battery?

The Cybertruck will be my first EV and I don’t want to get the GEN 3 installed too early, just in case Tesla releases a bigger/better charger. If the battery is north of 150 kHw, it would take awhile to charge up a low battery. At 150 kHw, your looking somewhere around 13 hours. At 180kHw, your looking at 15.5 hours.

Thoughts?
I would wait. They recently released the gen 3 with a longer cable. Also, it would probably be a good idea to make your home ready to accept any EV charger not just a tesla.
 

Ogre

Well-known member
First Name
Dennis
Joined
Jul 3, 2021
Threads
163
Messages
9,549
Reaction score
7,338
Location
Ogregon
Vehicles
Model Y
Country flag
With a 60 AMP breaker, you should be able to add more than 250 miles of charge per night.

That will top off the CT1 and the CT2 (assuming you have some reserves), and give you some pretty good mileage on the CT3.

The only way this is a big issue is if you frequently completely drain your battery and expect to do another 200+ mile trip the next day. I’m 8 months into Model Y ownership and only a bit frustrated with the much slower 110v/ 12 amp charger. If my state of charge is particularly low after a trip I just stop at a Supercharger for 10 minutes or so before coming home.
 
Last edited:

ajdelange

Well-known member
First Name
A. J.
Joined
Dec 8, 2019
Threads
4
Messages
3,064
Reaction score
1,622
Location
Virginia/Quebec
Vehicles
Tesla X LR+, Lexus SUV, Toyota SR5, Toyota Landcruiser
Occupation
EE (Retired)
Country flag
Do you think Tesla will release a GEN 4 Wall Connector for the Cybertruck due to the larger potential battery?
Would you also like to know the stock price 2 years out?

If the battery is north of 150 kHw, it would take awhile to charge up a low battery. At 150 kHw, your looking somewhere around 13 hours. At 180kHw, your looking at 15.5 hours.

Thoughts?
It isn't actually the size of the battery that matters but rather how far you drive in a day and what the vehicle's consumption turns out to be. That's probably going to be about 420 Wh/mi. If you drive 100 mi per day then you will have to load 42 kWh meaning you'll need 42/0.9 = 46.7 from the wall (90% charger efficiency0 which, at 11.5 kW (48A) would require 4.1 hr. That's not too bad. The other number to look at assumes that you keep it at 60% normally and an unexpected trip such comes up such that you want to get it to 90% for departure. That means adding 30%. If the battery is (TriMotor) 220 kWh (a reasonable estimate) that means 66 kWh which will take 66/(.9*11.5) = 6.4 hours more for a total of 10.5. Thus 48 A seems quite manageable for most cases. But will the market want faster than that? No question it would be a "nice to have". How would Tesla implement it?

As has been mentioned here Tesla has, in the past, sold cars that charged at 80 and 72A. Both of these required branch circuits of more than 60A and such a circuit requires a separate, lockable disconnect. Is it a coincidence that the manufacturers stopped offering EVSE that required feeders over 60A? I don't know. But how were those cars built? They had multiple chargers in them. The S's and X's had two 24 Amp chargers and with the fast charging option you got 3 for a total of 72. What is a DC fast charger? An assemblage of these chargers in an external cabinet. Thus for faster charging more charging modules are required but do they go in the car or in an external unit. We also have to look at the competition. Ford is evidently going to offer an EVSE that does V2H and charges at 80A. So it's obvious they have decided to put the modules in the EVSE and make them bi directional. Except that isn't what they have decided to do. They will apparently have the rectifiers in the truck and feed them 80A AC. Rivian is also talking about externally mouted EVSE that will do V2H. Again its obvious that this could be used as a DC charger but then who knows what they will come up with?

About a year ago I thought I knew the answer for Tesla. They would do for the CT what they do with the Semi and that is have multiple charge ports each with its own rectifier module(s). This neatly accommodates the customer with more than one Gen 3 HPWC (or any other 48A or 30A pair of EVSE by another manufacturer). The additional hardware/firmware required for the second port would be minimal and any solution that charges faster than 48A is going to required the extra charger modules anyway. This extra port would be a paid option and add extra flexibility in how one parks. Will they do anything like this? As a said at the outset you might as well ask me what the stock price will be.

For future proofing I'd say, as the others have, either wait or put a big subpanel in the charging area.
 

braddibbnd

Well-known member
First Name
Brad
Joined
May 1, 2020
Threads
0
Messages
55
Reaction score
35
Location
North Dakota
Vehicles
13 Ram, 24 CT AWD
Occupation
Retired
Country flag
[/QUOTE]
It isn't actually the size of the battery that matters but rather how far you drive in a day and what the vehicle's consumption turns out to be. That's probably going to be about 420 Wh/mi. If you drive 100 mi per day then you will have to load 42 kWh meaning you'll need 42/0.9 = 46.7 from the wall (90% charger efficiency0 which, at 11.5 kW (48A) would require 4.1 hr. That's not too bad. The other number to look at assumes that you keep it at 60% normally and an unexpected trip such comes up such that you want to get it to 90% for departure. That means adding 30%. If the battery is (TriMotor) 220 kWh (a reasonable estimate) that means 66 kWh which will take 66/(.9*11.5) = 6.4 hours more for a total of 10.5. Thus 48 A seems quite manageable for most cases. But will the market want faster than that? No question it would be a "nice to have". How would Tesla implement it?

As has been mentioned here Tesla has, in the past, sold cars that charged at 80 and 72A. Both of these required branch circuits of more than 60A and such a circuit requires a separate, lockable disconnect. Is it a coincidence that the manufacturers stopped offering EVSE that required feeders over 60A? I don't know. But how were those cars built? They had multiple chargers in them. The S's and X's had two 24 Amp chargers and with the fast charging option you got 3 for a total of 72. What is a DC fast charger? An assemblage of these chargers in an external cabinet. Thus for faster charging more charging modules are required but do they go in the car or in an external unit. We also have to look at the competition. Ford is evidently going to offer an EVSE that does V2H and charges at 80A. So it's obvious they have decided to put the modules in the EVSE and make them bi directional. Except that isn't what they have decided to do. They will apparently have the rectifiers in the truck and feed them 80A AC. Rivian is also talking about externally mouted EVSE that will do V2H. Again its obvious that this could be used as a DC charger but then who knows what they will come up with?

About a year ago I thought I knew the answer for Tesla. They would do for the CT what they do with the Semi and that is have multiple charge ports each with its own rectifier module(s). This neatly accommodates the customer with more than one Gen 3 HPWC (or any other 48A or 30A pair of EVSE by another manufacturer). The additional hardware/firmware required for the second port would be minimal and any solution that charges faster than 48A is going to required the extra charger modules anyway. This extra port would be a paid option and add extra flexibility in how one parks. Will they do anything like this? As a said at the outset you might as well ask me what the stock price will be.

For future proofing I'd say, as the others have, either wait or put a big subpanel in the charging area.
[/QUOTE]

All the numbers you've anticipated for the Cybertruck look like good assumptions(I'm hoping it might do a little better than 420 Wh/mi). And it will probably work for 70-80% of CT customers, but some of us will be using it as a truck constantly hauling and towing loads. Mine won't be a busy or long range hauler so looking at a 9.6kW charging setup. Of course those customers that do heavy work will easily save enough on fuel/maintenance that they can afford to install some sort of EVSE charging system. Just hoping Tesla will give a little guidance when they start production to get an idea of what might work best.
 
OP
OP
Carlos Thomas

Carlos Thomas

Well-known member
Joined
Nov 4, 2020
Threads
28
Messages
394
Reaction score
690
Location
San Antonio
Vehicles
Cybertruck
Country flag
This is a picture of my sub panel in the garage. Looks like I have some options to get a proper charge on the CT3. Any comments, much appreciated.

Tesla Roadster 2nd gen Tesla Wall Connector (Gen 4) for Cybertruck IMG_6634
 

Bigvbear

Well-known member
First Name
Justin
Joined
Apr 26, 2020
Threads
12
Messages
296
Reaction score
188
Location
Eugene, OR
Website
ts.la
Vehicles
2001 Chevy Tracker, 2018 Jeep Cherokee
Occupation
IT
Country flag
Couple of things. First off the wall connector is not a charger. Its a connection to the AC of the house. The charger is onboard the vehicle.

This may sound like semantics, but its not.

The Gen 2 wall connector was capable of 80 amp output, but only a few models of teslas could use that to it's full potential, the onboard charger kicked the amps down to what the vehicle was capable of using.

The gen 3 is (most likely) software limited to 48 amps right now and would most likely be able to deliver more after a firmware modification (odiously depending on your wiring feeding it)

last, most residential electrical service is 200 amps or less. So you are going to be limited by how many amps you can pump into the vehicle anyway. unless you want to brown out while charging your car.
 

Bigvbear

Well-known member
First Name
Justin
Joined
Apr 26, 2020
Threads
12
Messages
296
Reaction score
188
Location
Eugene, OR
Website
ts.la
Vehicles
2001 Chevy Tracker, 2018 Jeep Cherokee
Occupation
IT
Country flag
This is a picture of my sub panel in the garage. Looks like I have some options to get a proper charge on the CT3. Any comments, much appreciated.

IMG_6634.webp
the breaker on the far left of the picture says 50 amps, this appears to be a 100 amp capable subpanel but they only put a 50 amp breaker, probably due to the underlying wiring being used.

you can only do 80% of the rating of the circuit without risking overload and i see you already have four 20 amp and 1 15 amp 110 breaker using this. So appears to be maxed out.

You will need to upgrade it, get a certified electrician to give you a quote. Most likely you may have to upgrade the wiring coming to this subpanel (unknown what gage it is from the pic)
 

kev12345

Well-known member
First Name
Kevin
Joined
May 16, 2020
Threads
12
Messages
794
Reaction score
500
Location
Canada
Vehicles
Ram 1500
Country flag
I'm hoping they release a new backup gateway with a built in 2 way connector to mimic what ford has available. it'll simplify this mess quite a bit. no need for Powerwall, separate transfer switch and generator anymore for an entire home backup system. "get two birds stoned at once." - Ricky
Tesla Roadster 2nd gen Tesla Wall Connector (Gen 4) for Cybertruck 200am
 

Jhodgesatmb

Well-known member
First Name
Jack
Joined
Dec 1, 2019
Threads
82
Messages
5,201
Reaction score
1,986
Location
San Francisco Bay area
Website
www.arbor-studios.com
Vehicles
Tesla Cybertruck FS AWD, Tesla Model Y LR
Occupation
Retired AI researcher
Country flag
the breaker on the far left of the picture says 50 amps, this appears to be a 100 amp capable subpanel but they only put a 50 amp breaker, probably due to the underlying wiring being used.

you can only do 80% of the rating of the circuit without risking overload and i see you already have four 20 amp and 1 15 amp 110 breaker using this. So appears to be maxed out.

You will need to upgrade it, get a certified electrician to give you a quote. Most likely you may have to upgrade the wiring coming to this subpanel (unknown what gage it is from the pic)
The panel label says 100 amps. We are in the midst of increasing our service from 100 to 200 amps for the CT charger. We started the project last spring with the expectation that the CT would show up in about a year. We might have it all done before the rains come at which point all work will stop. Our driveway is over 200’ which has made things much more complicated and expensive. Point is, if you have to increase your service start the process now.
 

ajdelange

Well-known member
First Name
A. J.
Joined
Dec 8, 2019
Threads
4
Messages
3,064
Reaction score
1,622
Location
Virginia/Quebec
Vehicles
Tesla X LR+, Lexus SUV, Toyota SR5, Toyota Landcruiser
Occupation
EE (Retired)
Country flag
Couple of things. First off the wall connector is not a charger. Its a connection to the AC of the house. The charger is onboard the vehicle.
The wall connector is Electric Vehicle Support Equipment as described in section 625 of the NEC. It's job is to safely interface the charger in the vehicle to the mains which supply it.


The Gen 2 wall connector was capable of 80 amp output, but only a few models of teslas could use that to it's full potential, the onboard charger kicked the amps down to what the vehicle was capable of using.
The Gen 2 was capable of supporting up to 80 A charging from up to 4 HPWC on a single 100 A circuit. It had lugs big enough to accept No 3 (or maybe No. 2 - don't remember) and a charging cable capable of passing 80 A to a car (but it did get warm). It had a contactor capable of 80A and, most significantly, it communicated to the car that it could take up to 80A or less if it was commissioned for a smaller feeder or if there were multiple loads (more than 1 HPWC charging). Commissioning was by setting a small rotary switch.

The gen 3 is (most likely) software limited to 48 amps right now and would most likely be able to deliver more after a firmware modification (odiously depending on your wiring feeding it)
The Gen 3 HPWC is a less robust unit limited to 48A. It's terminal block is limited to No. 6. It's charging cable is substantially smaller than the Gen 2 cable consistent with 48A max vs 80. Its contactor is smaller. It to can be commissioned to 48A (or below). The max current limit signal it will send to the car is 48A provided that it has been commissioned for 48A and that there is only one car in the sharing pool. Commissioning and sharing are managed over WiFi rather than with hardware in the Gen2.


last, most residential electrical service is 200 amps or less. So you are going to be limited by how many amps you can pump into the vehicle anyway. unless you want to brown out while charging your car.
The limitation on what you can put into your panel is limited by what the inspector says you can put in there. Usually no eyebrows will be raised if the pole amperes are only a little over twice the panel rating e.g. a 200A panel (400 pole a,mperes) will generally get the thumbs up with less than 1000 pole amperes of breakers in it. An inspector may allow more or less depending on his assessment of the situation.
 